How should I size my breaker for a 20KVA 3phase UPS? Do I just times that by 1.25?
You didn't state voltage, but it'd be at least 20kVA/voltage/sqrt3. A UPS is typically not a continuous load (it may be energized for more than 3 hours but typically does not operate at max rated current over 3 hours) so no factoring by 125% for continuous load is required.How should I size my breaker for a 20KVA 3phase UPS? Do I just times that by 1.25?