Howdy forum.
I have a 4000W (4kw) laser cutter. Its massive and used for cutting up to 1" thick steel.
No job on the laser will be continuous or over 3 hours.
The KVA of the laser is 69KVA @ 208V = 199.85 Amps.
So using the next size up fuse rule, I would use a 200A fuses in a 200A enclosure.
Where I am getting tripped up is on the 80% vs 100% rating of OCPD. Its confusing.
I so rarely size OCPD on non-continuous loads that I am usually covered because I just multiply all the continuous loads by 1.25 and
therefore the fuses/disconnect are appropriately oversized for the fact that they are designed for 80% of their rating.
I spoke with Eaton and no enclosures (disconnects) are rated for 100% of the rated fuse value, only certain circuit breakers.
So my question is, am I ok with 200A fuses in a 200A enclosure for this dedicated circuit or do I need to use 200A fuses in a 400A disconnect to
correctly acknowledge the disconnect is only rated to allow the fuses to be used at 80% of their ampacity.
Thanks in advance.
I have a 4000W (4kw) laser cutter. Its massive and used for cutting up to 1" thick steel.
No job on the laser will be continuous or over 3 hours.
The KVA of the laser is 69KVA @ 208V = 199.85 Amps.
So using the next size up fuse rule, I would use a 200A fuses in a 200A enclosure.
Where I am getting tripped up is on the 80% vs 100% rating of OCPD. Its confusing.
I so rarely size OCPD on non-continuous loads that I am usually covered because I just multiply all the continuous loads by 1.25 and
therefore the fuses/disconnect are appropriately oversized for the fact that they are designed for 80% of their rating.
I spoke with Eaton and no enclosures (disconnects) are rated for 100% of the rated fuse value, only certain circuit breakers.
So my question is, am I ok with 200A fuses in a 200A enclosure for this dedicated circuit or do I need to use 200A fuses in a 400A disconnect to
correctly acknowledge the disconnect is only rated to allow the fuses to be used at 80% of their ampacity.
Thanks in advance.