I have been reviewing every bit of the NEC code possible to determine how to minimize the OCPD (Over Current Protection Device) size for an electrical panel containing many 2 HP motors controlled via VFDs (Variable Frequency Drive).
Typically over 50 3 HP VFDs will be used to control 1 to 2 HP motors on a 480 VAC 3-phase system. Both NEC and NFPA 79 state that the OCPD should be sized to be no smaller than the total FLA calculated + 125% FLA of largest load.
Assume a 3-HP VFD is rated at 5.6 FLA input while only driving a 1-HP motor at 1.85 FLA. Using the VFD rating for 50 motors plus a small 120 transformer, the OCPD required is larger than 350 Amps however, using real world continuous running loads the draw is never more than 130 Amps. Is there a way we can get an exception to NEC or NFPA79 based on historical data and use a smaller OCPD?
Thanks for your help,
Drew
Typically over 50 3 HP VFDs will be used to control 1 to 2 HP motors on a 480 VAC 3-phase system. Both NEC and NFPA 79 state that the OCPD should be sized to be no smaller than the total FLA calculated + 125% FLA of largest load.
Assume a 3-HP VFD is rated at 5.6 FLA input while only driving a 1-HP motor at 1.85 FLA. Using the VFD rating for 50 motors plus a small 120 transformer, the OCPD required is larger than 350 Amps however, using real world continuous running loads the draw is never more than 130 Amps. Is there a way we can get an exception to NEC or NFPA79 based on historical data and use a smaller OCPD?