I know that 100% noncontinuous load + 125% continuous load is used to size a branch circuit breaker if it is an 80% rated breaker, and 100% noncontinuous + 100% continuous if the circuit breaker is rated for 100%.
I also believe that I remember something in the NEC that used the actual size of all the circuit breakers to determine the size of the branch Circuit breaker. I'm not sure where I seen this, and it is driving me crazy. Is it for sizing a feeder and not a branch? The feeder has to be sized to not exceed the sum of all the breakers? If so, where is that located in the code?
I also believe that I remember something in the NEC that used the actual size of all the circuit breakers to determine the size of the branch Circuit breaker. I'm not sure where I seen this, and it is driving me crazy. Is it for sizing a feeder and not a branch? The feeder has to be sized to not exceed the sum of all the breakers? If so, where is that located in the code?