Understandable table 450.3(B) protection method can be
1) Primary protection only 125%
2) Primary and Secondary protection 250%
over 9A
480-240/120 1phase
Lets say I have a 10kVA transformer.
Ip=10k/480 = 20.8A
My primary protection should be 20.8X1.25 =26A so the next size up is 30A. What happened if the electrician installed a 50A breaker? is that acceptable for primary protection? It's that exceed the 1.25% requirement per table 450.3B.
Also does the wire needs to size to what size? 30A or 50A breaker?
over 9A
480-240/120 1phase
Ip=10k/480 = 20.8A