OCPD Transformer over protect?

Status
Not open for further replies.

thewire

Member
Location
Raleigh
Understandable table 450.3(B) protection method can be

1) Primary protection only 125%
2) Primary and Secondary protection 250%

over 9A
480-240/120 1phase
Lets say I have a 10kVA transformer.

Ip=10k/480 = 20.8A

My primary protection should be 20.8X1.25 =26A so the next size up is 30A. What happened if the electrician installed a 50A breaker? is that acceptable for primary protection? It's that exceed the 1.25% requirement per table 450.3B.

Also does the wire needs to size to what size? 30A or 50A breaker?
 
Understandable table 450.3(B) protection method can be

1) Primary protection only 125%
2) Primary and Secondary protection 250%

over 9A
480-240/120 1phase
Lets say I have a 10kVA transformer.

Ip=10k/480 = 20.8A

My primary protection should be 20.8X1.25 =26A so the next size up is 30A. What happened if the electrician installed a 50A breaker? is that acceptable for primary protection? It's that exceed the 1.25% requirement per table 450.3B.

Also does the wire needs to size to what size? 30A or 50A breaker?

The 50A primary breaker meets the 250% requirement for the primary OCPD for "primary and secondary protection."

The primary feeder should be sized for the 50A breaker.
 
The 50A primary breaker meets the 250% requirement for the primary OCPD for "primary and secondary protection."

The primary feeder should be sized for the 50A breaker.

So 26A *2.5 is 65A. So it's technically 2.5. What's the rule on the breaker size if we are following 1.25 and 2.5. Can they sized over 2.5, like 3X times or size between 1.25-2.5 is suffice?
 
So 26A *2.5 is 65A. So it's technically 2.5. What's the rule on the breaker size if we are following 1.25 and 2.5. Can they sized over 2.5, like 3X times or size between 1.25-2.5 is suffice?

20.8A * 2.5 is 52A. The primary breaker cannot be larger than 52A, so a 50A breaker is the largest breaker that can be used on the primary.
 
20.8A * 2.5 is 52A. The primary breaker cannot be larger than 52A, so a 50A breaker is the largest breaker that can be used on the primary.

yea. So they can't be larger than 2.5. it can be anything from 1.25-2.5. What If the breaker is 40A? Is this applicable? I am trying to understand how the 2.5 and 1.25 rules plays

Does it have to be either 1.25 or 2.5? can't be anything in between?
 
yea. So they can't be larger than 2.5. it can be anything from 1.25-2.5. What If the breaker is 40A? Is this applicable? I am trying to understand how the 2.5 and 1.25 rules plays

The primary breaker can be anything 50A or smaller, as long as it is larger enough to support the load. A 40A breaker would be fine.

If the primary breaker is larger than 125% (or the next size up ~ 30A in this example) then the secondary breaker must not be larger than 125% of the secondary rated current (or the next size up.)
 