Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
I’m being asked to provide 250A and 200A of power( they need that load/amperage in the field for temp power) in two different locations from two different panels.
Panels are 277/480v and will feed a step down xfrmr which will feed a120/208v panel.
They are telling me to price a new 200A and 250A breaker in the new 277/480v panels.
My thinking is that I don’t need that size breaker to feed the 277/480v step down xfrmr.
I could install either a 75 or 112kva xfrmr with the appropriate primary OCPD/wire and this would deliver power needed on the secondary side in the field.
Is my thinking correct? Thank you
Panels are 277/480v and will feed a step down xfrmr which will feed a120/208v panel.
They are telling me to price a new 200A and 250A breaker in the new 277/480v panels.
My thinking is that I don’t need that size breaker to feed the 277/480v step down xfrmr.
I could install either a 75 or 112kva xfrmr with the appropriate primary OCPD/wire and this would deliver power needed on the secondary side in the field.
Is my thinking correct? Thank you