OCPD

Status
Not open for further replies.
I currently ran power to a blower motor control panel, { a manual disconnect switch, a starter}.The motor FLA was 6.0 amps 3 phase, 480 Volt motor, I pulled #10 awg for a voltage drop THHN,I needed a 30 Amp CCt BKR in the panel, But my boss had told me that I needed A 70 amp bkr for the application, I thought that the Bkr protected the wire, if that is the case would A 70 Bkr be to much, Also does the bkr have to rated for start up current, Please respond.
 

bob

Senior Member
Location
Alabama
Re: OCPD

Look at table 430.52. You are allowd to go to 250% of the FLA of the motor. 2.5 x 6 amps = 15 amps when using an inverse time breaker. The breaker will only protect for short circuit. The thermal protection in the motor will protect for overloads.
 

bob

Senior Member
Location
Alabama
Re: OCPD

70 amps breaker is not correct. Boss may be thinking of another motor. Using table 450.150 the closest motor to the 6 amps listed is a 3 or 5 hp. Even at 208 volts neither the 3 or 5 hp would require a 70 amp breaker. You would have to goto a 20 hp to need a 70 amps breaker.
I think the Boss must be using the 30 amp ampacity for the #10 conductor. 30 x 2.5 = 75.

[ April 07, 2004, 12:58 PM: Message edited by: bob ]
 