Hello! First post.
I'm looking to protect a circuit that is powered by one phase of a three-phase WYE, the circuit is powered between hot and neutral on a 415V (phase-phase), 240V (phase-neutral) WYE where the neutral is solidly grounded.
240.60 (A)(2) makes it clear I can use a 300V fuse. But I want to use a 240V (non-slash rated circuit breaker).
From an Eaton document
-----------------
"
A straight rated OCPD (whether a fuse or circuit breaker) that protects
a single pole can be used to protect single-phase, line-to-neutral
loads when supplied from a three-phase, solidly grounded circuit. For
example, a 300 V rated fuse can be used to protect single-phase, line-
to-neutral loads when supplied from a three-phase, solidly grounded,
480/277 V circuit, where the single-phase, line-to-neutral voltage is 277
V. This is allowed in this application because a 300 V fuse will not have
to interrupt a voltage greater than its 300 V rating."
---------------
The NEC seems ambiguous; it doesn't seem to have the equivalent of 240.60 (A)(2) under the circuit breaker section.
So is it OK to use a 240V straight rated circuit breaker to protect a Single-phase line-to-neutral circuits supplied from a 3-phase, 4-wire, solidly grounded neutral source where the line-to-neutral voltage doesn't exceed 240V?
I'm looking to protect a circuit that is powered by one phase of a three-phase WYE, the circuit is powered between hot and neutral on a 415V (phase-phase), 240V (phase-neutral) WYE where the neutral is solidly grounded.
240.60 (A)(2) makes it clear I can use a 300V fuse. But I want to use a 240V (non-slash rated circuit breaker).
From an Eaton document
-----------------
"
A straight rated OCPD (whether a fuse or circuit breaker) that protects
a single pole can be used to protect single-phase, line-to-neutral
loads when supplied from a three-phase, solidly grounded circuit. For
example, a 300 V rated fuse can be used to protect single-phase, line-
to-neutral loads when supplied from a three-phase, solidly grounded,
480/277 V circuit, where the single-phase, line-to-neutral voltage is 277
V. This is allowed in this application because a 300 V fuse will not have
to interrupt a voltage greater than its 300 V rating."
---------------
The NEC seems ambiguous; it doesn't seem to have the equivalent of 240.60 (A)(2) under the circuit breaker section.
So is it OK to use a 240V straight rated circuit breaker to protect a Single-phase line-to-neutral circuits supplied from a 3-phase, 4-wire, solidly grounded neutral source where the line-to-neutral voltage doesn't exceed 240V?