Is there an error in the answer to Q13? It seems to me that the conductor should be #8 AWG according to Table 310.16.
Q13. What size wire and breaker is required for an air-conditioner whose nameplate specifies that the circuit conductor must have a minimum rating of 44A, with overcurrent protection not to exceed 60A. The terminals on the equipment are rated 75?C.
A. The branch-circuit conductors and short-circuit and ground-fault protection device must be sized according to the equipment?s nameplate [110.3(B)]. In this example, a 10 AWG conductor having a rating of 50A at the 75?C column of Table 310.16 [240.4(G)] protected by a 60A circuit breaker or fuse will be fine.
Q13. What size wire and breaker is required for an air-conditioner whose nameplate specifies that the circuit conductor must have a minimum rating of 44A, with overcurrent protection not to exceed 60A. The terminals on the equipment are rated 75?C.
A. The branch-circuit conductors and short-circuit and ground-fault protection device must be sized according to the equipment?s nameplate [110.3(B)]. In this example, a 10 AWG conductor having a rating of 50A at the 75?C column of Table 310.16 [240.4(G)] protected by a 60A circuit breaker or fuse will be fine.