Was reviewing a 120/240V 1-phase installation that seems odd. On the building exterior, there is 1 set of large service conductors (500MCM possibly) (2 phases and grounded (neutral)) that go thru the meter and enter a non-fused disconnect. Inside the disconnect, the neutral is bonded to 2 grounding electrodes. Leaving the disconnect are 2 sets of 2 phase conductors and neutral with each set going to a different 200A main breaker panel (size looks to be about a 250 MCM). Once you pull a panel cover, you will see the 2 phases and the neutral. It does not appear to be a ground ran to each panel, the conduit is PVC, and there are no ground rods installed at each panel. In each panel, the green bonding screw is installed to bond the neutral bus to ground bus.
I would think the main needs to be fused, would need a ground with each set, and would need to isolate the neutral and ground in each panel. Install is from the mid 90's.
I would think the main needs to be fused, would need a ground with each set, and would need to isolate the neutral and ground in each panel. Install is from the mid 90's.