Hi-end dual fuel Monogram range, manufacturers instructions say to install a 50A 240V circuit, namplate says 50A 240V (dual ovens are electric, cooktop gas).
Oddly the nameplate is not in kW and its 240V not a 120/240V circuit. I think every range I have ever seen was rated in kW.
So no problem easy math 50 X 240 = a 12kw range and per T220.55 column C it is 8kW so can be on a 8/2 NM 40A circuit (with a 50A receptacle& cord).
Or does 110.3(B) require a 50A circuit and 6/2 NM?
Oddly the nameplate is not in kW and its 240V not a 120/240V circuit. I think every range I have ever seen was rated in kW.
So no problem easy math 50 X 240 = a 12kw range and per T220.55 column C it is 8kW so can be on a 8/2 NM 40A circuit (with a 50A receptacle& cord).
Or does 110.3(B) require a 50A circuit and 6/2 NM?