electricaldoc
Member
210.4 Multiwire Branch Circuits.
(B) Dwelling Units. In dwelling units, a multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.
Would his apply to industry, and different voltages? If not is it a code requirement?
For example at my work I worked on a heater system. Where the power for heater comes from Hard wired 480V wye panelboard from several hundred feet away, and is ran threw emt. The control voltage 120v is supplied from a cord and plug. Which is dropped right out of the ceiling from soo cord from j box with EMT ran to 120V panelboard from several hounded feet the other direction. All power comes together in control box.
Now I can unplug 120v, and lock out 480v circuit breaker and all dead at once. So safe to work on, but is this a violation of code? If so which one?
Thanks in advance
Dan
(B) Dwelling Units. In dwelling units, a multiwire branch circuit supplying more than one device or equipment on the same yoke shall be provided with a means to disconnect simultaneously all ungrounded conductors at the panelboard where the branch circuit originated.
Would his apply to industry, and different voltages? If not is it a code requirement?
For example at my work I worked on a heater system. Where the power for heater comes from Hard wired 480V wye panelboard from several hundred feet away, and is ran threw emt. The control voltage 120v is supplied from a cord and plug. Which is dropped right out of the ceiling from soo cord from j box with EMT ran to 120V panelboard from several hounded feet the other direction. All power comes together in control box.
Now I can unplug 120v, and lock out 480v circuit breaker and all dead at once. So safe to work on, but is this a violation of code? If so which one?
Thanks in advance
Dan