Hey everyone,
Maybe someone can enlighten me on this one here out of one of Mikes Books 2008 NEC Exam Prep:
pg 254 if you have the book
* Number of 15 Ampere Circuits Example
question: How many 15A circuits are required for a 2,000 sq ft dwelling unit?
step 1: general lighting VA = 2,000 sq ft x 3 VA
general lighting VA = 6,000 VA
Step 2: General Lighting Amperes
I = VA/E
therefore I = 50VA
Step 3: Determine the number of circuits
number of circuits = General Ltg Amps / Circuit Amps
number of circuits = 50A / 15A
number of circuits = 3.3 or 4 circuits rounded up.
That is what the book says. But can you really have 15A loaded on a 15A breaker because the 15 amp breaker in the house is not going to be rated for continuous duty therefore it would be really rated for only 12 amps of which could be occuring on a circuit no problem for more than 3 hours if someone plugged in a portable heater etc etc.. thefore it would be:
number of circuits = 50A / 12A
number of circuits = 4.16 or 5 circuits rounded up.
The other thing I find interesting is you de-rate a range oven over 12 KW. If you are cooking large items in a large oven for more than 3 hours wouldn't that be an item that would need a rating of continuous duty?
Ideas?
Maybe someone can enlighten me on this one here out of one of Mikes Books 2008 NEC Exam Prep:
pg 254 if you have the book
* Number of 15 Ampere Circuits Example
question: How many 15A circuits are required for a 2,000 sq ft dwelling unit?
step 1: general lighting VA = 2,000 sq ft x 3 VA
general lighting VA = 6,000 VA
Step 2: General Lighting Amperes
I = VA/E
therefore I = 50VA
Step 3: Determine the number of circuits
number of circuits = General Ltg Amps / Circuit Amps
number of circuits = 50A / 15A
number of circuits = 3.3 or 4 circuits rounded up.
That is what the book says. But can you really have 15A loaded on a 15A breaker because the 15 amp breaker in the house is not going to be rated for continuous duty therefore it would be really rated for only 12 amps of which could be occuring on a circuit no problem for more than 3 hours if someone plugged in a portable heater etc etc.. thefore it would be:
number of circuits = 50A / 12A
number of circuits = 4.16 or 5 circuits rounded up.
The other thing I find interesting is you de-rate a range oven over 12 KW. If you are cooking large items in a large oven for more than 3 hours wouldn't that be an item that would need a rating of continuous duty?
Ideas?