Re: # of conductors in a 3/4" conduit
Don't forget 240.4(B) allows a 60 amp breaker (Next standard breaker size) on #6 NM as long as the min. circuit ampacity is 55 or less.
And a #10 EGC is all you need per 250.122.
Since you lost your book:
240.4(B) Devices Rated 800 Amperes or Less The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used , provided all of the following conditions are met:
(1) The conductors being protected are not part of a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
240.6 Standard Ampere Ratings
(A) Fuses and Fixed-Trip Circuit Breakers The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60 ...
Table 250.122 Minimum Size Equipment Grounding Conductors...
60 Amps: #10 copper
My guess is you could probably get away with pulling 2 # 6's and 3 # 10's, but I'd have to know the Min. Cir. Ampacities first.