Can I get 2 #4's and 3#8's copper in 3/4" emt or pvc? I just realized today that I lost my code book. Have to put a new furnace in the house. Thanks
 
Re: # of conductors in a 3/4" conduit

Assuming you mean THHN... those conductors have a cross sectional area totalling .2746 square inches. That would mean 1" EMT or PVC40. That seems like a weird combination of conductors to me.
 
Re: # of conductors in a 3/4" conduit

residential, one 60 amp breaker and one 30 amp breaker with one #8 for the ground. Single phase 240 volt.
 
Re: # of conductors in a 3/4" conduit

Is 60 & 30 the Maximum Overcurrent sizes?
What's the Min. Circuit Ampacity for these units?
You might be able to run smaller conductors.
 
Re: # of conductors in a 3/4" conduit

I assume that the breakers in the furnace are maximum over current protection. I haven't seen the unit yet, but just wanted to get ready for it. It will be here Wed or Thurs. I have 1/0 al at the old furnace now, but it's under the house and would like copper to the unit instead of installing a sub-panel then short circuit runs to the furnance, being it is under the house. But with the price of copper now, and I'm buying material retail, I might go with the sub-panel. I think the furnace is 15kw. I haven't done residential for 26 years, so I'm a little rusty in that part.
 
Re: # of conductors in a 3/4" conduit

Don't forget 240.4(B) allows a 60 amp breaker (Next standard breaker size) on #6 NM as long as the min. circuit ampacity is 55 or less.
And a #10 EGC is all you need per 250.122.

Since you lost your book:

240.4(B) Devices Rated 800 Amperes or Less The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used , provided all of the following conditions are met:
(1) The conductors being protected are not part of a multioutlet branch circuit supplying receptacles for cord-and-plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.

240.6 Standard Ampere Ratings
(A) Fuses and Fixed-Trip Circuit Breakers The standard ampere ratings for fuses and inverse time circuit breakers shall be considered 15, 20, 25, 30, 35, 40, 45, 50, 60 ...


Table 250.122 Minimum Size Equipment Grounding Conductors...
60 Amps: #10 copper

My guess is you could probably get away with pulling 2 # 6's and 3 # 10's, but I'd have to know the Min. Cir. Ampacities first.
 
Re: # of conductors in a 3/4" conduit

Originally posted by bark:
I think the furnace is 15kw. I haven't done residential for 26 years, so I'm a little rusty in that part.
Forget KW ratings! Tha factory will calculate the Min Cir Amps and Max Overcurrent for you!

Min. Cir. Amps determines the size of wire.
Max. Overcurrent determines breaker size.
Just be sure to use the 240 Volt specs!
 
Re: # of conductors in a 3/4" conduit

Wait a sec! 15 KW! looks like it will be over 55 amps!
Nevermind! :(

15,000 / 240= 62.5 plus the blowers etc...

Sorry, you probably will need the #4's, but #10 for the 30 amp unit and EGC should work.

.0814
.0814
.0243
.0243
.0243
-----
.2357

40% 0f a 3/4" EMT is .213

Still no good
:(

Hopefully it's not a 15KW!

[ January 01, 2006, 08:22 PM: Message edited by: davedottcom ]
 
Re: # of conductors in a 3/4" conduit

The hvac contractor thought it was at least 15kw. I thought it was 20 kw. I'm not to sure if adding a subpanel under the house is legal. It won't be gfci but just for the hvac equipment, a light,and a recepticle.
 
Re: # of conductors in a 3/4" conduit

can you run larger conduit??? if I was pulling the wire I would :) Code is minimum size I go larger just for my ease of installation if I can get away with it
 