I’ve often wondered what the relationship is between the length of or “rings” of porcelain that make-up a distribution line insulator to the voltage of the lines. Is there a rule-of thumb?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I’ve often wondered what the relationship is between the length of or “rings” of porcelain that make-up a distribution line insulator to the voltage of the lines. Is there a rule-of thumb?
I imagine it's really about surface distance, so both the quantity and diameter affect voltage rating.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
with my local utilities, I have always used a ball park of 1 ring =5kV to ground on systems 24.9kV L-L and higher. But there are usually too many variable for this to be used universally.
 