Here's a question from the Holt 2020 Exam Prep book, commercial section:
My question is this:
Though the question clearly calls out computers and printers as some of the loads, I would think that they would be included in the receptacle loads described in the question. But in the provided solution, the book adds all the specified loads including all the receptacles PLUS the computers and printers. I "get it" from a can-you-do-the-math perspective, but I'm wondering about this practically. Wouldn't the Master and the AHJ assume that computers and printers would be normal loads on the receptacles in such a building? Would they really make some estimate of the number of computers and printers for doing the load calcs? Why not count the number of pinball machines and mini fridges that tenants could possibly plug in?
Asking for a friend.
My question is this:
Though the question clearly calls out computers and printers as some of the loads, I would think that they would be included in the receptacle loads described in the question. But in the provided solution, the book adds all the specified loads including all the receptacles PLUS the computers and printers. I "get it" from a can-you-do-the-math perspective, but I'm wondering about this practically. Wouldn't the Master and the AHJ assume that computers and printers would be normal loads on the receptacles in such a building? Would they really make some estimate of the number of computers and printers for doing the load calcs? Why not count the number of pinball machines and mini fridges that tenants could possibly plug in?