hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch I have 208V/120V three phase system at Panel A. Panel A circuit A-29 has 2 poles circuit breaker and circuit A-28 has 2 poles circuit breaker.
I have plans that show whip 8 wire furniture system wiring schematic as shown on attached sketch which shows 6 receptacles for 6 cubicals fed from circuit A-28 phase A and neutral N and 6 receptacles 6 cubicals from A-29 from phase B and same neutral N. A-28 has wire 2#12 + 1#12G and A-29 has wire 2#12+1#12G total of six wires.
I am not sure if the schematic is wired correctly but have following questions:
1. Would I need handle ties multiwire branch circuit A-28 and A-29 per code?
2. Should not all 12 cubical receptacles be wired from 2 pole breaker circuit A-28 to avoid handle ties?
3. The wires going to furniture from Panel A are six wires. Should not the wires be 3#12+1#12G for A-28 and 3#12+1#12G for A-29 to make it 8 wires?
I have plans that show whip 8 wire furniture system wiring schematic as shown on attached sketch which shows 6 receptacles for 6 cubicals fed from circuit A-28 phase A and neutral N and 6 receptacles 6 cubicals from A-29 from phase B and same neutral N. A-28 has wire 2#12 + 1#12G and A-29 has wire 2#12+1#12G total of six wires.
I am not sure if the schematic is wired correctly but have following questions:
1. Would I need handle ties multiwire branch circuit A-28 and A-29 per code?
2. Should not all 12 cubical receptacles be wired from 2 pole breaker circuit A-28 to avoid handle ties?
3. The wires going to furniture from Panel A are six wires. Should not the wires be 3#12+1#12G for A-28 and 3#12+1#12G for A-29 to make it 8 wires?
Attachments
Last edited: