bigpapa400lb
Member
I'm trying to figure out this question.
An office building with 2500 sq has 42 general purpose receptacle outlets. What is the minimum number of two wire, 120v 20 amp branch circuits required to supply the total lighting and receptacle load for this office?
Answer key says 8 but I forgot how to calculate from table 220.12.
So how do you figure out the 8 circuits?
An office building with 2500 sq has 42 general purpose receptacle outlets. What is the minimum number of two wire, 120v 20 amp branch circuits required to supply the total lighting and receptacle load for this office?
Answer key says 8 but I forgot how to calculate from table 220.12.
So how do you figure out the 8 circuits?