I don't frequently wire these freestanding partitions, but did note the code change for 2005 that requires a common disconnecting means for multiwire branch circuits feeding these partitions.
Typically, the whips contain 5 conductors. (3 hots, neutral and ground)
Some of the newer partitions have an 8 conductor whip which adds another hot, neutral and iso. ground.
I am being asked to supply UPS power to the separate set of conductors.
As I see it, the code will not allow this due to an inability to simultaneously disconnect all ungrounded conductors feeding the partition since they will be from separate panelboards.
Thoughts?
Before you get started,,, I do hate these things and they weren't at all my choice, but gotta pay the bills.
Typically, the whips contain 5 conductors. (3 hots, neutral and ground)
Some of the newer partitions have an 8 conductor whip which adds another hot, neutral and iso. ground.
I am being asked to supply UPS power to the separate set of conductors.
As I see it, the code will not allow this due to an inability to simultaneously disconnect all ungrounded conductors feeding the partition since they will be from separate panelboards.
Thoughts?