I haven't done and commercial load calc in a while. Just want to make sure I haven't missed anything.
Noncontinuous - 100% - 1st - 10kVA 50% - remainder
Warehouse & Office recepts 24*180VA
Continuous - 100%
Office lighting 1200ft² * 3VA/ft²
Warehouse lighting 3500ft² * ¼VA/ft²
A/C1 22969VA
A/C2 8112VA
A/H2 1920VA
Walk-in A/H 334VA
Walk-in Comp 2414VA
Non Cont = 4320VA
Continuous = 39951VA
Total = 44271
÷ 208V/3P = 123A