Oh Boy!!! Resi. Pool

Merry Christmas
Status
Not open for further replies.

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
In between jobs and was handed this today. 3 LED pool lights and 2 controlers. Here is a pic and link. Anybody install these? Nothing in the
install instructions or on web-site about this being a listed transformer. Called tech support and they said:

Oh yeah, there desinged for pools.

No UL listing. I'm thinking I have issues with 680.23(A)(2).

What do you think? They are 12V LED's.

View attachment 1583
 
Dennis Alwon said:
Chris they are ETL approved so they are listed.

Thanks Dennis, they are listed. If I remember correctly that tranny should be labled for use with pools and spas. I don't sse that.
 
Here it is.

(2) Transformers. Transformers used for the supply of underwater luminaires, together with the transformer enclosure, shall be listed as a swimming pool and spa transformer. The transformer shall be an isolated winding type with an ungrounded secondary that has a grounded metal barrier between the primary and secondary windings.
 
I don't see anywhere in 680.23(A)(2) that says the transformer should be label. It must be listed for pools and I believe it is simply through the info on the page. It is called a pool light and is listed by ETL-- I wouldn't worry about it.
 