Hello members,
In the spirit of the recent thread supplying Electrical Service to Detached Garage I, too, would like your comments for a project that I will be submitting to our city building dept.
I am preparing plans to install a new 200 A metered / load panel on our detached garages (owned by the Homeowners Assoc) .
PoCo will commit to a 200 A service drop.
Since this panel is installed on a detached garage, it seems that I need to account for temperature correction in the riser. In other words, a 2/0 is not acceptable.
Is the following calculation overly conservative?
3/0 awg ampacity derate, correction / adjustment factors
(1) 90°F Rating of Conductor (T-310.15(8)(16)) for 3/0 awg XHHW = 225 A
(2) 90°F Temp Correction Factor (T-310.15(B)(2)(a)) with RMT wall mounted = 0.91
(3) Conduit Fill Factor (T-310.15(B)(3)(a)) two current-carrying conductors = 1.0
3/0 awg ampacity derate = (1) x (2) x (3) = 225 A x 0.91 x 1.0 = 204 A
Ampacity derate > panel main breaker rating: 204 A > 200 A (acceptable)
In the spirit of the recent thread supplying Electrical Service to Detached Garage I, too, would like your comments for a project that I will be submitting to our city building dept.
I am preparing plans to install a new 200 A metered / load panel on our detached garages (owned by the Homeowners Assoc) .
PoCo will commit to a 200 A service drop.
Since this panel is installed on a detached garage, it seems that I need to account for temperature correction in the riser. In other words, a 2/0 is not acceptable.
Is the following calculation overly conservative?
3/0 awg ampacity derate, correction / adjustment factors
(1) 90°F Rating of Conductor (T-310.15(8)(16)) for 3/0 awg XHHW = 225 A
(2) 90°F Temp Correction Factor (T-310.15(B)(2)(a)) with RMT wall mounted = 0.91
(3) Conduit Fill Factor (T-310.15(B)(3)(a)) two current-carrying conductors = 1.0
3/0 awg ampacity derate = (1) x (2) x (3) = 225 A x 0.91 x 1.0 = 204 A
Ampacity derate > panel main breaker rating: 204 A > 200 A (acceptable)