tryinghard
Senior Member
- Location
- California
I have a heater that is labeled 3PH 440V 3000W, it was manufactured in 1964.
We have been rewiring a unit that actually includes 4 of these and just for kisses and giggles I checked the resistance. My results are 118 ohms from A-B, B-C, & A-C on each heater.
I think these elements are losing resistance through use and age. The branch is currently a 480V 30A circuit, if the 118 ohms holds true after warm up I should read 28 amperes, I know this will be the final test.
BUT if Ohms = E squared / P shouldn?t I read 194 ohms? I understand reading resistance cold may be lower than reading resistance heated up, but would it be this much? Any advice/opinions?
We have been rewiring a unit that actually includes 4 of these and just for kisses and giggles I checked the resistance. My results are 118 ohms from A-B, B-C, & A-C on each heater.
I think these elements are losing resistance through use and age. The branch is currently a 480V 30A circuit, if the 118 ohms holds true after warm up I should read 28 amperes, I know this will be the final test.
BUT if Ohms = E squared / P shouldn?t I read 194 ohms? I understand reading resistance cold may be lower than reading resistance heated up, but would it be this much? Any advice/opinions?