Oil field grounding

Status
Not open for further replies.

beanland

Senior Member
Location
Vancouver, WA
NETA

NETA

Check NETA to see what they may have. It may not be oil field specific, though. Most testing specs I have seen are written specifically for the application and circumstances.
 

beanland

Senior Member
Location
Vancouver, WA
IEEE 81

IEEE 81

IEEE 81 deals with determining the resistivity of earth. That tells you nothing about whether the grounding system was designed, installed, and maintained to perform a needed function. Fall of potential tests are useful but not sufficient. Current injection testing is needed to verify the integrity and performance of the grid itself. DLRO testing can be useful to test the quality of connections.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
API

API

This might be a start:

RP 2003
Protection Against Ignitions Arising Out of Static, Lightning, and
Stray Currents
Presents the current state of knowledge and technology in the fields of static
electricity, and stray currents applicable to the prevention of hydrocarbon
ignition in the petroleum industry and is based on both scientific research
and practical experience. The principles discussed in this RP are applicable
to other operations where ignitable liquids and gases are handled. Their use
should lead to improved safety practices and evaluations of existing
installations and procedures. Pages: 76
7th Edition | January 2008 | Product Number: K20037 | Price: $125.00
You may access RP 2003 in a read-only platform: publications.api.org
 