Recently asked if this install is NEC compliant.
1.Industrial setting
2.Type SJOOW cord
3.120vac busway located at ceiling with recepts in busway
4.Equipment 120vac tool grinder
They want to run a cord from the busway (plugged in at the busway) down to a recep. mounted on a support beam to plug in the tool grinder. After reading 400.7 and 400.8 I come to the conclusion that this is ok. This cord will also be fastened to the support beam and at first reading 400.8(4) it seems this would not be allowed but under 368.56(B)(1) to me this allows it. My only concern would be that this cord will be supplying a mounted recep that will be used by the tool grinder but the possibility of something else being plugged in exists. So basically it will be supplying the recep. Your thoughts would be appreciated. Thanks Guys!
1.Industrial setting
2.Type SJOOW cord
3.120vac busway located at ceiling with recepts in busway
4.Equipment 120vac tool grinder
They want to run a cord from the busway (plugged in at the busway) down to a recep. mounted on a support beam to plug in the tool grinder. After reading 400.7 and 400.8 I come to the conclusion that this is ok. This cord will also be fastened to the support beam and at first reading 400.8(4) it seems this would not be allowed but under 368.56(B)(1) to me this allows it. My only concern would be that this cord will be supplying a mounted recep that will be used by the tool grinder but the possibility of something else being plugged in exists. So basically it will be supplying the recep. Your thoughts would be appreciated. Thanks Guys!