Well, have an interesting project I am currently working on and just want to get some thoughts. The project I am working on is an existing manufacturering facility with a 204/120V 3-phase system and utilizes 2 utility transformers. This tells me I am dealing with an open delta center tapped system and that a high leg exists. Utility power goes into a main board then distributes out to serveral other panels, some 3-phase and some 1-phase. Regular receptacle / lighting loads are mixed throughtout all the panels.
We are designing an addition and I will be serving the addition with a new 480/277 service. I will then abandon the current 240 open delta service entrance and re-feed the existing main 240v 3-phase panel as a sub-feed from the 480V system via a step-down transformer. Now, here is where I am questioning the connection. I know the overall KW demand of the 240V system from past utility bills and will be metering in the future to determine KVA and Power factor. However, how do I go about determining the transformer size? I will not be able to determine the percentage of existing 1 pole loads verses the 3 phase loads and If I remember correctly, I am limited to 5% of the KVA rating for 1 pole loads because of the neutral. Maybe I am confusing the 5% with someting else.
That is my first question. My second question now involves the power in the addition. In the addition, I will have 480V equipment (no problem) and 240 3-phase equipment (problem). Since there is 240V 3-phase equipment, the obvious choice is to set a 240V 3-phase panel for the 3-phase equipment and receptacles / general 1-pole loads. But, now I am dealing with the same thing as I am dealing with on the existing system and the 5% rule. So, to combat that, what if I ran with a transformer to go from 480 to 240 closed delta, corner grounded. This will give me 240V power and I can come out of the 240V panel to another transformer and set a 240/120 1-phase panel for 1-pole loads? DOes this make sence?
Any thoughts would be great.
We are designing an addition and I will be serving the addition with a new 480/277 service. I will then abandon the current 240 open delta service entrance and re-feed the existing main 240v 3-phase panel as a sub-feed from the 480V system via a step-down transformer. Now, here is where I am questioning the connection. I know the overall KW demand of the 240V system from past utility bills and will be metering in the future to determine KVA and Power factor. However, how do I go about determining the transformer size? I will not be able to determine the percentage of existing 1 pole loads verses the 3 phase loads and If I remember correctly, I am limited to 5% of the KVA rating for 1 pole loads because of the neutral. Maybe I am confusing the 5% with someting else.
That is my first question. My second question now involves the power in the addition. In the addition, I will have 480V equipment (no problem) and 240 3-phase equipment (problem). Since there is 240V 3-phase equipment, the obvious choice is to set a 240V 3-phase panel for the 3-phase equipment and receptacles / general 1-pole loads. But, now I am dealing with the same thing as I am dealing with on the existing system and the 5% rule. So, to combat that, what if I ran with a transformer to go from 480 to 240 closed delta, corner grounded. This will give me 240V power and I can come out of the 240V panel to another transformer and set a 240/120 1-phase panel for 1-pole loads? DOes this make sence?
Any thoughts would be great.