Old apt complex. Panel question

Status
Not open for further replies.

TheCrow

Member
Location
Mk
Occupation
Electrical
32 bank meter s. Each meter is feeding a federal Pacific 2 pole main breaker rated at 30 amps. Customer wants panel changed out .Going to change wire size 60 amps. Could u leave it at 30 amps .
 
If you're asking if it's okay to use a 30a breaker on wire rated for more, the answer is yes.
 
Well, some jurisdictions require a minimum service size for new installations.
I suspect they would not enforce that on rewires of existing installations. But the only way to tell for sure would be to ask the AHJ.
 
Status
Not open for further replies.
Top