mpross

Senior Member
Location
midwest
Does anybody recognize this breaker? I am looking to replace this with a GFI breaker if possible. Any thoughts?

Other option is to re-stamp mounting plate so that a GFI outlet will fit, but the customer really likes the idea of having a GFI breaker...

Thanks in advance!
Matt
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
yes thats old Frank, why not take off the cover and look at the sticker? GFI should fit if the manuf. is still around.
 

mpross

Senior Member
Location
midwest
Remove Cover

Remove Cover

I couldn't take anything apart at the time... figured I could rely on someone to help me out :)

Thanks!
 

480sparky

Senior Member
Location
Iowegia
Here's the pix for those who don't want to click on the link:

OldBreaker.jpg



I would say it's a Generous Electric.

Although I would change the EMT fitting on the top, too.​
 

hurk27

Senior Member
I would say also that is a GE 1" stab (Bryant style) in a Mid West Electric receptacle tap box. many of the Mid West box's were UL listed for several breaker manufactures, including GE, Bryant, CH (BR series) ITE/Siemens, and a few more that used these type breakers. if this is in fact a Mid West box, then any GFCI breaker from the above will work.;)

Also this is common to see in an industrial building, where a receptacle was needed and is tapped off the crane rail power
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
As the others have said, that's a standard 1" size, and any approved standard GFCI breaker should fit just fine.
 