Apparently alum was used, not Cu. (say 4-700 mcm Al);
then if RMC, 40% = 4.004 in2. That's not even enough
for the 4.404 in2 of the 4-700's. I'll have to verify if
the C. is 4" instead of 3.5". How easily would the EGC be
installed? Apparently, the cost is up for grabs.
A 1/0 Cu EGC increases it to 4.6263 in2, < 5.153 in2 for 4" RMC.