I'm looking to get clarification on 406.3 (D)(3)(b). I understand that replacing a 2 prong receptacle with a GFCI receptacle will satisfy this rule. If you have old 2 wire NM, there is nothing to bond the GFCI to. What if you have old BX without the bonding wire. The steel sheath/metallic box will give you 120v line to ground. My understanding for replacing it with newer AC was that if a ground fault occurs the old BX which has a higher impedance, will not clear the fault as an EGC would. My question is should the GFCI receptacle be bonded to the metallic jb/BX? I realize the GFCI doesn't need to be grounded to protect, but is there an issue if it gets bonded to a higher impedance "ground" like the old BX/metal jb?