Wahoo20:
Are there any individual manual wall switches? If there are, then you need isolated contacts to each RR7 from the replacement for the rotary switch.
If the rotary switch was just a way to turn on and off a large number of loads approximately at the same time, but reduce load inrush current on the electrical system, or to reduce the load on the 24 V supply, then you need some sort of sequencer.
How many total RR7s are switched by this rotary switch?
A sample of one RR7 has a per coil resistance of about 55 ohms. DC minimum voltage to change state is about 22 V, or about 0.4 A. A more normal DC voltage to use would likely be 30 V DC. In my house I use 38 V DC, the peak voltage of a GE transformer for the RR stuff. Has worked well for 46 years. My relays are the older RR low number.
Where do you go from here. If all the relays are good, and you say they are, then what does GE have that does the equivalent of the rotary switch? That would be the simplest. If not, then the number of relays that need to be switched becomes important along with whether or not there are any individual wall switches.
.