travmad804
Member
- Location
- USA Virginia
[FONT="]I have an old Reliance inverter that is being upgraded to a new VFD. I am familiar with the functions of a VFD and have troubleshot and changed parameters in them etc. but I have never installed one myself from scratch. I plan to demo the components use the existing inverter enclosure and mount the drive inside the cabinet.[/FONT]
[FONT="]What I have....[/FONT]
[FONT="]480V 40HP 48A (52FLA) motor on a blower for an air handler controlled by a thermostat. The motor has a fused disconnect and the inverter is being fed from a 100A breaker and is protected with 200A fuses in the enclosure. [/FONT]
[FONT="]My thoughts are that I can install an Allen Bradley PowerFlex 750 480V 60HP VFD 20F11ND077AA0NNNNN in place of the old inverter and other than a means of locking disconnect on the outside of the enclosure door and a 24v power supply for the thermostat control what else will I need? I know the NEC requires a way of protecting the motor (fused disconnect) and the drive (100A breaker) and obvious grounding, wire size etc.[/FONT]
[FONT="]Do I need overload protection between the drive and the 100A breaker or is overload protection already built into the drive? Should I protect the VFD with a fused disconnect, if so what size fuses? Do I need a a soft start or starter/bypass starter?[/FONT]
[FONT="]I know the VFD acts as a soft start by ramping the frequency and Im assuming I can control the speed by adjusting HZ and creating a set point parameter in the VFD that it will ramp the motor up to once the thermostat tells it to turn on. Can I wire the thermostat to a set of contacts on the drive for start/stop of the motor?
Is there anything Im missing? Should just be able to install the VFD with minimal components from what Im thinking. Any help is welcome.[/FONT]
[FONT="]What I have....[/FONT]
[FONT="]480V 40HP 48A (52FLA) motor on a blower for an air handler controlled by a thermostat. The motor has a fused disconnect and the inverter is being fed from a 100A breaker and is protected with 200A fuses in the enclosure. [/FONT]
[FONT="]My thoughts are that I can install an Allen Bradley PowerFlex 750 480V 60HP VFD 20F11ND077AA0NNNNN in place of the old inverter and other than a means of locking disconnect on the outside of the enclosure door and a 24v power supply for the thermostat control what else will I need? I know the NEC requires a way of protecting the motor (fused disconnect) and the drive (100A breaker) and obvious grounding, wire size etc.[/FONT]
[FONT="]Do I need overload protection between the drive and the 100A breaker or is overload protection already built into the drive? Should I protect the VFD with a fused disconnect, if so what size fuses? Do I need a a soft start or starter/bypass starter?[/FONT]
[FONT="]I know the VFD acts as a soft start by ramping the frequency and Im assuming I can control the speed by adjusting HZ and creating a set point parameter in the VFD that it will ramp the motor up to once the thermostat tells it to turn on. Can I wire the thermostat to a set of contacts on the drive for start/stop of the motor?
Is there anything Im missing? Should just be able to install the VFD with minimal components from what Im thinking. Any help is welcome.[/FONT]