MrJLH

Senior Member
Location
CO
Anyone have a low down on who took over Nelson Electric. Looking for info an an old Nelson 4101 Starter. Need to swap out a thermal overload relay as only two phases are protected.
 
Anyone have a low down on who took over Nelson Electric. Looking for info an an old Nelson 4101 Starter. Need to swap out a thermal overload relay as only two phases are protected.

Why worry about it? Just buy a new 3 phase separately mounted OL relay from your favorite source and wire it in. Nelson was bought by General Signal, who was then bought by OZ Gedney decades ago, who was then bought by Emerson. The only parts of Nelson that Emerson kept are the Heat Trace and Fire Stop products, all else was dumped though the years of changing hands. No support remains for the old stuff.
 
Why worry about it? Just buy a new 3 phase separately mounted OL relay from your favorite source and wire it in. Nelson was bought by General Signal, who was then bought by OZ Gedney decades ago, who was then bought by Emerson. The only parts of Nelson that Emerson kept are the Heat Trace and Fire Stop products, all else was dumped though the years of changing hands. No support remains for the old stuff.


The problem is the starter is in a NEMA 7 enclosure and the client wont open it for fear of an incident. What I need to do is connect a new motor to this starter but my experience with this older type of starter is there is only two overloads on the motor feeders and no protection on the control circuits. I need to prove this to them before I can even think to open the enclosure and none the less make the recommendation to replace it with out proving this to them.
 
The problem is the starter is in a NEMA 7 enclosure and the client wont open it for fear of an incident. What I need to do is connect a new motor to this starter but my experience with this older type of starter is there is only two overloads on the motor feeders and no protection on the control circuits. I need to prove this to them before I can even think to open the enclosure and none the less make the recommendation to replace it with out proving this to them.

How can you connect a new motor to this starter without opening it?

Proving what to them, that it is no longer legal to use an OL relay with heaters on only two legs? That's in the NEC. They are "grandfathered" in with the old style so long as nothing is changed, but changing the motor is something that usually triggers the loss of that allowance.
 
Oh wait, sorry, I get it now. You BELIEVE you are going to find an old starter with two OL heaters inside, which will stop you from finishing the job because you can't reconnect to it, so you want to know in advance if that's what it will have.

As I recall, Nelson didn't ever make the actual motor starters, I think they used Westinghouse (also gone now but still supported by Eaton). If the motor starter is not older than around 1976, then it's going to have 3 OL heaters in it. See if they have records about when they installed that system. If it was ion the 80s or newer, it's a no brainer. If it is older than 1980 (being conservative here) you could be prepared with a Westinghouse OL relay, I'm pretty sure you can still get them from Eaton as replacement parts. It might be expensive and if you don't use it, make sure you can return it, or just charge them for it anyway as a precautionary expense.
 
Oh wait, sorry, I get it now. You BELIEVE you are going to find an old starter with two OL heaters inside, which will stop you from finishing the job because you can't reconnect to it, so you want to know in advance if that's what it will have.
Yeah, I have worked round enough of this old style equipment to just know this. Also is the issue of protection of the control circuit which typically is no protected with this older style of equipment.

As I recall, Nelson didn't ever make the actual motor starters, I think they used Westinghouse (also gone now but still supported by Eaton). If the motor starter is not older than around 1976, then it's going to have 3 OL heaters in it. See if they have records about when they installed that system. If it was ion the 80s or newer, it's a no brainer. If it is older than 1980 (being conservative here) you could be prepared with a Westinghouse OL relay, I'm pretty sure you can still get them from Eaton as replacement parts. It might be expensive and if you don't use it, make sure you can return it, or just charge them for it anyway as a precautionary expense.

I have an old drawing that calls out a Nelson starter with a catalog number but ebay and google turn up nothing.
 