jmsbrush
Senior Member
- Location
- Central Florida
Today Installed 120' of Emt for some new lighting. This Pharmacy is very old.
The service is 60Amps.
Now I know the code will allow 2 EGC's in one slot in the grounding bus bar,
but you can only put 1 Neutral conductor in one slot of the Neutral buss bar? Why is that? Its all going back to the same Place.
On old panels the neutral and ground's are all tied in togther anyway.
Every slot already had two or 3 conductors going in them.
So what do you do in a case like this?
There was absolutely no room to install another buss bar, The owner will not do and upgrade. Any thoughts?
The service is 60Amps.
Now I know the code will allow 2 EGC's in one slot in the grounding bus bar,
but you can only put 1 Neutral conductor in one slot of the Neutral buss bar? Why is that? Its all going back to the same Place.
On old panels the neutral and ground's are all tied in togther anyway.
Every slot already had two or 3 conductors going in them.
So what do you do in a case like this?
There was absolutely no room to install another buss bar, The owner will not do and upgrade. Any thoughts?