250-140. Frames of Ranges and Clothes Dryers
This section shall apply to existing branch-circuit installations only. New branch-circuit installations shall comply with Sections 250-134 and 250-138. Frames of electric ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and outlet or junction boxes that are part of the circuit for these appliances shall be grounded in the manner specified by Section 250-134 or 250-138; or, except for mobile homes and recreational vehicles, shall be permitted to be grounded to the grounded circuit conductor if all of the following conditions are met.
1. The supply circuit is 120/240-volt, single-phase, 3-wire; or 208Y/120-volt derived from a 3-phase, 4-wire wye-connected system.
2. The grounded conductor is not smaller than No. 10 copper or No. 8 aluminum.
3. The grounded conductor is insulated, or the grounded conductor is uninsulated and part of a Type SE service-entrance cable and the branch circuit originates at the service equipment.
4. Grounding contacts of receptacles furnished as part of the equipment are bonded to the equipment.