I know from reading all the threads on the subject that you can put a receptacle above a suspended ceiling but you can't have anything permanently plugged into it. fine.
A colleague just suggested an alternative to me that sounds reasonable and with code;
He suggests putting a Nema 1 Box above the suspended ceiling and installing the receptacle in it. Then run a 1 1/2 nipple to the suspended ceiling. Put a protective bushing on conduit where it exits the ceiling and plug in at will.
My comment to him was why not just put the receptacle on the ceiling. His comment back was he had worked with architects that prefered seeing the hole of the conduit.
What say you?