This is what I'm dealing with:
An old gym, they have a concession stand, this past weekend they blew fuses like crazy. I went there and found this set up.
60 amp 120/240 subpanel with main and range and 4 plug fuses.
This is fed from a main panel (3 phase 120/208v) by an old AL 3 wire cable. OCPD at main is not marked, so i'm assuming is a 60 amp breaker.
They need more circuits to provide for the electrical demand for a series of appliances.
At this moment all 4 fuses are occupied with 4 different circuits.
I need a bigger panel with more circuits, i will need at least 5 or 6 120v circuits and a 240v for a Range.
I thought about putting a 100 amp subpanel right where this subpanel is, so in that case I won't have to run new feeder, eliminating cost and making customer happy.(Of course he wants this as cheap as possible)
My questions are:
1- As long as i leave the same OCPD at the main protecting the AL wires it wouldn't matter to use a 100 amp subpanel, Right?
2- How would you provide the 240 v for the range out of this subpanel with 208v going in? ( I suppose with a transformer, what kind?, what kind of hook-up?)
3-Is it illegal to use a 120/240v subpanel if i have 208v from the main panel?
Thank you all.
An old gym, they have a concession stand, this past weekend they blew fuses like crazy. I went there and found this set up.
60 amp 120/240 subpanel with main and range and 4 plug fuses.
This is fed from a main panel (3 phase 120/208v) by an old AL 3 wire cable. OCPD at main is not marked, so i'm assuming is a 60 amp breaker.
They need more circuits to provide for the electrical demand for a series of appliances.
At this moment all 4 fuses are occupied with 4 different circuits.
I need a bigger panel with more circuits, i will need at least 5 or 6 120v circuits and a 240v for a Range.
I thought about putting a 100 amp subpanel right where this subpanel is, so in that case I won't have to run new feeder, eliminating cost and making customer happy.(Of course he wants this as cheap as possible)
My questions are:
1- As long as i leave the same OCPD at the main protecting the AL wires it wouldn't matter to use a 100 amp subpanel, Right?
2- How would you provide the 240 v for the range out of this subpanel with 208v going in? ( I suppose with a transformer, what kind?, what kind of hook-up?)
3-Is it illegal to use a 120/240v subpanel if i have 208v from the main panel?
Thank you all.