When upgrading a service on an old home wired with the old armored cable (no internal bonding strip) I usually cut the AC in the attic right where it goes down to the old fuse panel so I can move the old circuits to the new service panel outside. This requires a j-box in the attic to continue on to the new panel with NM. I normally ground the j-box with the grounding wire from the romex, but this creates another problem. There is continuity thru the armor to the metal j-box then on to the panel via the romex. Does this violate 333-19 & 250-2(d)(99 NEC)? Should I cut the grounding conductor off the romex to break the path? I have heard of fires being started during a ground fault due to the high resistance path on the unbonded armor not allowing enough current to reach the OCPD. It?s hard to determine which is the lesser of 2 evils. Also the armor was continuous to the old fusebox for many years before. I am curious how others deal with this. Thanks for any help on this.