goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
I recently had a service call to repair wiring to an AC compressor. An aluminum SE cable was used to power the 40 amp unit. It was run inside the condo walls and ran (in open air) to the compressor for about 12 feet to a disconnect mounted on the side of the unit. A (makeshift)wooden enclosure was built to cover both the condensor and power lines. This was typical for all the condo units. It seems that 17 years ago (when this condo complex was built) a siding contractor drove a nail through an SE cable feeding the AC unit. As far as I can tell the initial penetration went through one of the phase conductors and burnt a portion of the braided EGC. The nail also partially penetrated the insulation of the second phase conductor. After all this time the insulation finally broke down and burnt up the cable.
My question is whether aluminum SE cable was ever allowable by the NEC for this purpose and installed in this manner. The whole installation seemed shoddy to me but somehow they managed to build an entire complex this way.
My question is whether aluminum SE cable was ever allowable by the NEC for this purpose and installed in this manner. The whole installation seemed shoddy to me but somehow they managed to build an entire complex this way.