So I have some locations on a job where the wall are existing and we'd like to use these boxes instead of having to cut open the wall and use a 4-11/16" box with supports to the studs. I'm thinking the engineer is going to reject them as them won't offer the strength and support as using a 4-11/16 box with stud support. I'm going to write an RFI and try and make a case. Anything you can think of that may make the case to use these in the capacity they will not rip out of the wall when devices plugged into the receptacle.

1691518680427.png


1691518705816.png
 
While I haven't had that problem, you could use old-work boxes that are designed to be attached to studs.

1691520613789.png 1691520631198.png
 
Last edited:
I have used them with F straps and as long as you get the straps tight and no one is too rough with them they will last but I have had a few get loose and wobbly.
 
And where exactly is that requirement found?
Here:


Metallic outlet boxes for use in fire rated wall assemblies include single and double gang metallic outlet and switch boxes equipped with Listed metallic or nonmetallic cover plates. These outlet boxes are intended for installation in bearing and non-load bearing wood or steel stud gypsum wallboard walls with fire resistance ratings of 2 hours or less. The metallic outlet or switch boxes must be securely fastened to the studs. Openings in the wallboard facing are to be cut so that the clearance between the box and wallboard does not exceed 1/8 inch. The surface area of individual metallic outlet or switch boxes must not exceed 16 square inches. In addition, the entire surface area of the boxes must not exceed 100 square inches per 100 square feet of wall surface.
 
Personally I don't like anything that only attaches to only drywall or plaster. Maybe they weren't installed properly, or maybe rough usage. Maybe because I see too many of then used in DIY or handyman work. I just see so many of them loose and full of hackwork.
 
Personally I don't like anything that only attaches to only drywall or plaster.
I agree with this. Cutting the wallboard and patching is much easier than people imagine.

If you pre-make patches and cut your holes to match, it is easy put in the new box (mounted to the stud) and then seal things up. Splurge on adjustable depth mudrings and make it easy to match everything up.

-Jon
 
I agree with this. Cutting the wallboard and patching is much easier than people imagine.

If you pre-make patches and cut your holes to match, it is easy put in the new box (mounted to the stud) and then seal things up. Splurge on adjustable depth mudrings and make it easy to match everything up.

-Jon
Yeah people abuse receptacles a lot. Kids and pets knock corded stuff down, plugs get yanked sideways. I hate the cheepo receptacles too, they get loose quick from any kind of abuse.
 