A bit embarrassed to admit it but I don't know what terminals on this old xfmr mean with regard to primary (input), secondary (output) and what (how) to connect line and load sources to those appropriate terminals. Hope I'm in the right thread for answers to my question.

From what I've been able to find on the internet this transformer was made by or for Reliance Electric long ago...probably WW2 era. While I'm used to a xfmr primary (input) connection wiring being on one side and the secondary (load) wiring on the other, this transformer does not have wires as such, but terminals firmly embedded on both sides.
Those terminals are labeled H1 thru H6 (both sides of body winding) and X1, X2 also on both sides of the body winding. There is a plate on top with 4 wire strapping schemes designated 207-227, 228-252, 414-454, and 456-504. That plate with "H" letters also has L1 and L2 letters at certain H letters points. I am assuming the wiring strap schemes indicate which H terminals to strap appropriate for the line source. So for example if I wanted to connect the primary to a line source of 220VAC I would use the strap scheme of 207-227 indicated on the top plate and connect 220VAC 2 input wires to each one of the 2 terminal straps for that range.

As for the load (output) winding I am assuming terminals X1 and X2 (marked on the winding body but NOT on the top plate. So if I wanted to connect my load I would connect it to X1 and X2 marked terminals. As for the load voltage (which is not indicated anywhere) I can always meter that with an appropriate resistance connected across X1 and X2. I'm actually looking for 24 step down volts but of course don't yet know if this xfmr secondary winding actually is 24 VAC.

I would be happy to attach a photo of all xfmr views if that could helpful for ID. Thanks for any help.
 

topgone

Senior Member
Thanks, am trying to do that now

Use the lowest connection diagram-->
  1. connect 480V line1 on H1, connect H3 and H4, then
  2. connect 480V line 2 on H6.
  3. Then measure the voltage between terminals X1 and X2.


If you get 24V, then you are correct in guessing it's 24VAC.
 

just the cowboy

Inactive, Email Never Verified
Location
newburgh,ny
don't forget the jumpers

don't forget the jumpers

A bit embarrassed to admit it but I don't know what terminals on this old xfmr mean with regard to primary (input), secondary (output) and what (how) to connect line and load sources to those appropriate terminals. Hope I'm in the right thread for answers to my question.

From what I've been able to find on the internet this transformer was made by or for Reliance Electric long ago...probably WW2 era. While I'm used to a xfmr primary (input) connection wiring being on one side and the secondary (load) wiring on the other, this transformer does not have wires as such, but terminals firmly embedded on both sides.
Those terminals are labeled H1 thru H6 (both sides of body winding) and X1, X2 also on both sides of the body winding. There is a plate on top with 4 wire strapping schemes designated 207-227, 228-252, 414-454, and 456-504. That plate with "H" letters also has L1 and L2 letters at certain H letters points. I am assuming the wiring strap schemes indicate which H terminals to strap appropriate for the line source. So for example if I wanted to connect the primary to a line source of 220VAC I would use the strap scheme of 207-227 indicated on the top plate and connect 220VAC 2 input wires to each one of the 2 terminal straps for that range.

As for the load (output) winding I am assuming terminals X1 and X2 (marked on the winding body but NOT on the top plate. So if I wanted to connect my load I would connect it to X1 and X2 marked terminals. As for the load voltage (which is not indicated anywhere) I can always meter that with an appropriate resistance connected across X1 and X2. I'm actually looking for 24 step down volts but of course don't yet know if this xfmr secondary winding actually is 24 VAC.

I would be happy to attach a photo of all xfmr views if that could helpful for ID. Thanks for any help.

Yes you would hook up to the spots marked L1 + L2 with line voltage and install jumpers as shown.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Several on-line sources show that transformer number as being a 120VAC secondary. 24VAC secondary would be rare at 150VA, and there are a lot of these showing on FleaBay and Amazon being sold as used or New Old Stock (NOS), likely because they were spare parts that sat in inventory somewhere and were never used. Reliance got out of the transformer business maybe 25-30 years ago.

Be careful trusting it, a lot can happen to old dried insulation that has been sitting around that long..
 