This is somthing that I ran into and havent seen in a while and thought I should post it so others will know not to do this.
If you ever run into an old Zinco meter/main panel that is made for trailers and campers the one with the 50 amp 240v 4-wire receptacles on the front, under the slide up cover. "DONT EVER REMOVE THE COVER" without turning off all the breakers as this panel has a stab on the neutral for the branch feeders that when you remove the cover the neutral is lost but the hots are not and you will float the neutral and cause alot of damage to the customers appliances.
I dont know why this type of panel was ever allowed but it was. and is a very dangerous panel.
Maybe I should of posted this in safty but I wanted it to be read thats why I posted it here.
If you ever run into an old Zinco meter/main panel that is made for trailers and campers the one with the 50 amp 240v 4-wire receptacles on the front, under the slide up cover. "DONT EVER REMOVE THE COVER" without turning off all the breakers as this panel has a stab on the neutral for the branch feeders that when you remove the cover the neutral is lost but the hots are not and you will float the neutral and cause alot of damage to the customers appliances.