R Rsauls New member Location Atlanta, Georgia Jul 20, 2016 #1 In the 1988 NEC Code, was it a code back then as it is now to have the 120vac Breaker feeding a Fire Alarm System or equipment shall not supply any other loads?
In the 1988 NEC Code, was it a code back then as it is now to have the 120vac Breaker feeding a Fire Alarm System or equipment shall not supply any other loads?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Jul 20, 2016 #2 There was no 1988 NEC. There was 1987 and 1990. I don't think that rule was in the code until the 2008 code.
There was no 1988 NEC. There was 1987 and 1990. I don't think that rule was in the code until the 2008 code.