older disconnect rated 10,000 RMS

Status
Not open for further replies.

Andy22

Member
Location
Wyoming
I want to use an older disconnect rated 10,000 RMS. If the interrupting rating of the fuses is adequate does the enclosure need to meet the interrupting rating? I assume it does but want to be sure. Thanks!
 
The device (disconnect) would need to be rated for the available current also.
 