Ok, when using a Kenny clamp on XFMR’s where typically I would pass the GEC through the grounding lug to X0 or take it straight to X0 and add a bonding jumper, does a Kenny clamp eliminate the need for that?
Thanks!
 
I can’t help myself….

a7a06bc2be9dc82f5b0398f8a5dce015.jpg
 
Do you know if this is accepted by the code book?
the code is not going to address a part by name. The point is to meet the intent of the code, you are using a listed part as intended.
 