I have been running into this a lot lately. With Inverter, transfer switch, and main service panel installed indoors, typically in a basement area, I usually install a wiring trough below the equipment to simplify the paths between components and keep it neat and organized. But typically the utility still wants an outside accessible solar disconnect. To accomodate the utility and to serve as the Rapid shutdown switch, I like to install a lockable disconnect outside, and just run a single conduit through the wall from the wiring trough. The only conductors needed in the switch are the L1 and L2 conductors, and an EGC. I understand 300.3(B) specifies all conductors of the same circuit and, where used , the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, etc. However, the Neutral is not used in the outside disconnect, and the disconnect only serves to de-energize the L1 and L2 conductors. Running the neutral out from the gutter in the conduit with the L1 and L2 and switched L1 and L2 conductors out to the switch and back serves no purpose. I cannot think of an issue with OCPD with this arrangement either. If there were a Ground fault on L1 or L2 in the path, the OCPD protecting the path would trip, with the fault current returning through the bonding jumper at the service. If there were a Line to line fault, ditto. I appreciate any thoughts or opinions on this situation.