I have had an ?off grid? house for about 15 years. It is PV and wind powered (with batters and so on). I?m running 2 linkable inverters that each make 35 amps at 240 volts. Both inverters have there own 30 amps CB that is screwed in to the panel board this is on a 200 amp panel. I have a 200 amp CB that is running 4/0 SER in to my house about 50 feet away in a 4? PVC pipe to a 200 amp panel where all of my house hold circuits are.
Last week I had an ?on grid? system put in. It is a parallel 200 amp service (400 amp meters). It was also put in to the shed. The power company wanted to use a 400 amp service because down the road I will want to sell of power. The electrician put in a 200 amp panel in the shed and a 200 amp CB is running 4/0 SER in to my house about 50 feet away in a 4? PVC pipe to a 200 amp panel. My heat, AC, range, and water heater are in this panel.
I wanted to be able to switch my well between the ?off grid? and ?on grid? systems. So he put in a 100 amp generator panel. The panel he put in only switches the 2 hot wirers. Ever since he put in the new system I have been having problem with voltages on both systems. I did have him come back out and remove the wiring from the ?off grid? system to the generator panel and the voltages have been fine since.
The grounding for the ?off grid? system is. A ground rod at both of the wind turbines. A ground ring in the shed. A ground rod outside the shed for the PV panels. They are all #2 copper that run into the 200 amp panel in the shed. There is also a ground jumper between the -24 volt batter system and the panel. The panel is also bonded to the water pipe. Around my house there is a ground ring that goes in to the 200 amp sub panel it is also bonded to the water pipe in side the house. This was done about 15 years ago and has not changed.
When the electrician put in the new panel in the shed he put in a ground rod because of the power company. And also ran#4 copper between the 2 panels in the shed. In the house he ran a #4 copper between the 2 sub panels.
-If I get a generator transfer switch that will switch the neutrals as well will, keep my voltage problem from happening?
-I do not understand why the voltage problems happened.
-Why would an electrician no go by the plans that the inspector and utility engineers signed for my house? If he was trying to be cheep he charged me $6000 and the PVC was already there. I know the materials only cost $1359 at HD if I would have gotten them.
-Yes I am NOT an electrician but there is one that did the work and any changes needed.
I have had an ?off grid? house for about 15 years. It is PV and wind powered (with batters and so on). I?m running 2 linkable inverters that each make 35 amps at 240 volts. Both inverters have there own 30 amps CB that is screwed in to the panel board this is on a 200 amp panel. I have a 200 amp CB that is running 4/0 SER in to my house about 50 feet away in a 4? PVC pipe to a 200 amp panel where all of my house hold circuits are.
Last week I had an ?on grid? system put in. It is a parallel 200 amp service (400 amp meters). It was also put in to the shed. The power company wanted to use a 400 amp service because down the road I will want to sell of power. The electrician put in a 200 amp panel in the shed and a 200 amp CB is running 4/0 SER in to my house about 50 feet away in a 4? PVC pipe to a 200 amp panel. My heat, AC, range, and water heater are in this panel.
I wanted to be able to switch my well between the ?off grid? and ?on grid? systems. So he put in a 100 amp generator panel. The panel he put in only switches the 2 hot wirers. Ever since he put in the new system I have been having problem with voltages on both systems. I did have him come back out and remove the wiring from the ?off grid? system to the generator panel and the voltages have been fine since.
The grounding for the ?off grid? system is. A ground rod at both of the wind turbines. A ground ring in the shed. A ground rod outside the shed for the PV panels. They are all #2 copper that run into the 200 amp panel in the shed. There is also a ground jumper between the -24 volt batter system and the panel. The panel is also bonded to the water pipe. Around my house there is a ground ring that goes in to the 200 amp sub panel it is also bonded to the water pipe in side the house. This was done about 15 years ago and has not changed.
When the electrician put in the new panel in the shed he put in a ground rod because of the power company. And also ran#4 copper between the 2 panels in the shed. In the house he ran a #4 copper between the 2 sub panels.
-If I get a generator transfer switch that will switch the neutrals as well will, keep my voltage problem from happening?
-I do not understand why the voltage problems happened.
-Why would an electrician no go by the plans that the inspector and utility engineers signed for my house? If he was trying to be cheep he charged me $6000 and the PVC was already there. I know the materials only cost $1359 at HD if I would have gotten them.