I have an inspector telling me that he "thinks" that the following installation is not code allowed. I asked him for a code reference that says that we are not supposed to do this, but he is asking me for a reference stating that it is allowed. Anyway,...
We did a line side tap of a service as allowed by 2011NEC 705.12(A) (2013 California code). Our tap conductors are routed from the switchboard to a gutter above the disconnect within 10' of the switchboard. From the gutter one single conduit is routed to a fused disconnect for the PV system. This one conduit has the tap conductors and the PV system AC feeders.
The inspector is saying that we need two conduits. One per circuit. So that if the disconnect is OFF, it will be easy to tell which circuits are ON and which ones are OFF.
Can anyone think of a code reference that prohibits this installation?
We did a line side tap of a service as allowed by 2011NEC 705.12(A) (2013 California code). Our tap conductors are routed from the switchboard to a gutter above the disconnect within 10' of the switchboard. From the gutter one single conduit is routed to a fused disconnect for the PV system. This one conduit has the tap conductors and the PV system AC feeders.
The inspector is saying that we need two conduits. One per circuit. So that if the disconnect is OFF, it will be easy to tell which circuits are ON and which ones are OFF.
Can anyone think of a code reference that prohibits this installation?