One family dwelling RV attachment receptacle!

K1llah03z

Member
Location
Florida
Occupation
Electrician
This might be a rabbit hole. I’ve asked a few inspectors and they are all telling me that’s great question! Do RV attachment receptacles need to be GFCI protected per 2020 nec. I could argue the fact the 210.8 does not apply because this attachment receptacle is not a branch circuit. A branch circuit is The circuit conductors between the final overcurrent device protecting the circuit and the outlet. If RVs have their own ocpd inside the Rv that would make the wire feeding the receptacle a feeder. Is there any clarification on this subject?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
What the unit equipment has onboard in the way of OCPD's does not matter, the premise wiring defines the feeder or branch circuit. Many items that plug into receptacles have miniature circuit breakers or fuse protection.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
What the unit equipment has onboard in the way of OCPD's does not matter, the premise wiring defines the feeder or branch circuit. Many items that plug into receptacles have miniature circuit breakers or fuse protection.
I was thinking the same thing, my Christmas lights have integral fuse protection. The wiring and receptacle are still a branch circuit. Certainly something other than an RV can be plugged into the receptacle.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In our department's infinite wisdom they have ruled that a listed RV receptacle and enclosure such as the ones manufactured by Milbank is "utilization equipment" and no GFCI is required. If it's simply a 30 or 50 amp "off the shelf" receptacle then GFCI is required.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Woa, that is great. IDK how that was rationalized,but OK!
Just a tad of sarcasm in case it was missed.
We installed a Midwest receptacle, as you describe, a few years ago but protected it with GFCI. A few days later the customer plugged in a bastardized camper trailer turned into a ‘Food Trailer’. Saved someone a very nasty shock at the least.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
In our department's infinite wisdom they have ruled that a listed RV receptacle and enclosure such as the ones manufactured by Milbank is "utilization equipment" and no GFCI is required. If it's simply a 30 or 50 amp "off the shelf" receptacle then GFCI is required.
If they are addressing something like bellow I can see it making sense, you would basically be feeding a sub panel and the branch circuit would start there.

1707058597673.png
However, I don't think that was what the OP was asking about.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
This might be a rabbit hole. I’ve asked a few inspectors and they are all telling me that’s great question! Do RV attachment receptacles need to be GFCI protected per 2020 nec. I could argue the fact the 210.8 does not apply because this attachment receptacle is not a branch circuit. A branch circuit is The circuit conductors between the final overcurrent device protecting the circuit and the outlet. If RVs have their own ocpd inside the Rv that would make the wire feeding the receptacle a feeder. Is there any clarification on this subject?
This has been finally been made clear in 551.71(F) in the 2023 edition. GFCI is not required in an RV pedestal for the 30 or 50 amp receps.
What is still not clear is whether the would apply outside of an RV park in, say, a dwelling. In my view it should because, as you say, these outlets are really feeders when used with an RV. I would just require the RV receps to be in a listed RV panel and pass it.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
In my view it should because, as you say, these outlets are really feeders when used with an RV.
So in your view Rob's Christmas lights changes his receptacle branch circuit to a feeder?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
So in your view Rob's Christmas lights changes his receptacle branch circuit to a feeder?
No, this would clearly be wrong. I'm saying that the CMP has determined that in an RV park the 30 and 50 amp site receps in a listed RV panel are for feeders to an RV and no GFCI is required. Prior to the 2023 edition this far less clear.
I also implied that this would not likely meet the letter of the code outside of an RV park at a dwelling.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
So in your view Rob's Christmas lights changes his receptacle branch circuit to a feeder?
It would if it had a UL 489 Circuit Breaker in it. But certainly it instead has a UL 1077 Supplementary Protector in it.

See the Article 100 definitions for "Overcurrent Protective Device, Branch-Circuit" and "Overcurrent Protective Device, Supplementary."

Cheers, Wayne
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
No, this would clearly be wrong. I'm saying that the CMP has determined that in an RV park the 30 and 50 amp site receps in a listed RV panel are for feeders to an RV and no GFCI is required. Prior to the 2023 edition this far less clear
Yes the 2023 did add some wording regarding the 30 and 50 amp receptacles. The 2020 also had the same requirements just that the wording is less clear.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
551.71 is in Part VI. Recreational Vehicle Parks and should not apply to a receptacle at a dwelling. The dwelling receptacle would fall under the standard 210.8 rules.
Aren't the GFCI requirements for 15A & 20A, 120V? The RV is a 30A receptacle. I'm not speaking of the new requirements for 240V, 50A circuits.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
What the unit equipment has onboard in the way of OCPD's does not matter, the premise wiring defines the feeder or branch circuit. Many items that plug into receptacles have miniature circuit breakers or fuse protection.
Yes, but those are supplementary overcurrent protective devices. That would not change the definition for a branch circuit.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yes, but those are supplementary overcurrent protective devices. That would not change the definition for a branch circuit.
Ok, so let's forget the OCPD issue and say I install a 4 wire range receptacle outside for a portable outside kitchen or my brothers RV when he comes to visit. Under the current code does it require GFCI protection? Is it a branch circuit or a feeder as far as the inspector is concerned?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Aren't the GFCI requirements for 15A & 20A, 120V? The RV is a 30A receptacle. I'm not speaking of the new requirements for 240V, 50A circuits.
Since this is a dwelling 210.8(F) applies.
210.8(F) Outdoor Outlets.
All outdoor outlets for dwellings, other than those covered in 210.8(A)(3), Exception to (3), that are supplied by single-phase branch circuits rated 150 volts to ground or less, 50 amperes or less, shall have ground-fault circuit-interrupter protection for personnel.
 