W wireday Senior Member Location New England Occupation Master electrician May 3, 2022 #1 One 30amp 2 pole breaker feeding out to two walk-in coolers, each cooler has its own disconnect. Been running fine for years, any code issue?
One 30amp 2 pole breaker feeding out to two walk-in coolers, each cooler has its own disconnect. Been running fine for years, any code issue?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor May 3, 2022 #2 No, as long as the units' numbers (MCA/MOCP) are being met. You're describing a typical feeder.